Commercial ejector vent size is _____ inches, but if the ejector pit is within _____ feet of a 3 in vent stack the vent can be _____ inches.

Prepare for the Kentucky Journeyman Plumbing Test with comprehensive quizzes and practice questions. Delve into plumbing fundamentals and specific state regulations. Enhance your skills and pass with confidence!

Multiple Choice

Commercial ejector vent size is _____ inches, but if the ejector pit is within _____ feet of a 3 in vent stack the vent can be _____ inches.

Explanation:
Ejector pits need proper venting so air can enter and traps don’t siphon when the ejector pumps discharge. The standard vent size for a commercial ejector vent is 3 inches. But if the ejector pit is within 25 feet of a 3-inch vent stack, that larger vent can share the venting so the ejector vent itself can be reduced to 2 inches. Beyond 25 feet, you wouldn’t rely on the stack alone, so you’d keep the 3-inch vent. So the correct statement is: 3 inches, within 25 feet, the vent can be 2 inches.

Ejector pits need proper venting so air can enter and traps don’t siphon when the ejector pumps discharge. The standard vent size for a commercial ejector vent is 3 inches. But if the ejector pit is within 25 feet of a 3-inch vent stack, that larger vent can share the venting so the ejector vent itself can be reduced to 2 inches. Beyond 25 feet, you wouldn’t rely on the stack alone, so you’d keep the 3-inch vent. So the correct statement is: 3 inches, within 25 feet, the vent can be 2 inches.